No doubt the nettle of ac/dc change-over at Reading will need to be grasped one day but at present all that is needed is, I believe, 3 substations and 5 TSC's. Platforms 4a,b (and c one day) will do.
The separation of ac / dc traction can be done in a number of ways the 2 used by
NR» are 25 kV isolation transformers typically 2 per track the isolation sections spread over about half a mile, track circuits are isolated by
IBJs▸ in both rails at a number of points along with complex earthing and voltage limiting devices between the 2 earth systems (the dc earth and the ac earth)
How is the Reading Spur - Reading New Jn line isolated at present?
It isn't in the sense of ac dc electrification, usual practice in dc traction areas is to use ac track circuits and in ac areas to use dc track circuits as the
GWML▸ is not electrified at Reading immunisation can be achieved by the use of ac track circuits.
The isolation between ac and dc traction is not only for track circuit immunisation there are other problems such as stray traction return current that can cause the other form of traction current switchgear, transformers etc problems