The main drawback of fuses is the absolute requirement for an ample stock of spares, an intermittent fault can blow a surprising number of fuses before it is located.
As demonstrated on Friday afternoon.
What is wrong with fuses?
Fuses BS88 (
HRC▸ ) fuses are very reliable, can handle high fault levels, work as well with dc and ac and are not susceptible to nuisance tripping due to mechanical vibration like
MCBs▸ also easy to grade in terms of discrimination.
MCB are used in places and the new signalling power supplies (650V) uses
VCBs▸ and a auto reconfigurable system, however for the lower voltage parts of the system fuse are the most reliable.
The incoming supply from the
DNO▸ or internal railway high voltage transformers will be a BS88 (type) fuse.
[/quote]
I suggest we ask ourselves how we would prefer critical electrical circuits to be protected in civil airliners.
There's about three minutes to rectify a problem.....
OTC
[/quote]
The biggest problem I have come across in my 40 years as an electrical engineer is you can only reset a MCB a number of times after it has cleared a fault (typically after 5 faults) this is because the contacts get pitted and burnt and then there is the risk of contacts welding, also MCB are expensive compared to the humble "red spot" BS88.
The railway signalling system and many other critical system has hundreds of thousands if not millions of fuse 99.9% of them sit there passively for their working life for 30, 40 even 50 years doing their job and retire without a rupture, the ones that do rupture do so because there has been a fault.
A fault is just that something has gone wrong and its not the fuse that ruptured because it felt like it its because a cable or component has failed, to get a system up and running new fuse are put in if they rupture again then the fault has to have detailed investigation because if you just keep putting fuses in more and more damage is done and can even lead to loss of life or fire